(I fired the kiln up to about 2100 F by having my gas pressure as high as it would go with no standing flame from the vent)

You say you are adjusting gas presure-is this with the meter regulator?

after that you say you turn it up-I'm confused its already on max? you said

Or a presure regulator somewhere else?

Or is this just the single valve to kiln? and its full on 

In terms of reduction that small flame out top does not mean the whole kiln is reducing. I can get a flame out of my 12 cubic upodraft with hardly any reduction in middle or bottom. To get that I need the damper in some. 

The damper need to be part of the cycle.

The only way to keep the bottom from overfiring is to use a damper

It sounds like you are still just barley getting enough gas down that long 3/4 inch gas line. Can you adjust your meter presure with a manometer ?do you know how to do that?This is a 1/4 pound presure (7inchs on a monometer right)

 