Setting up my kiln, venting


Honeyhas6

Recommended Posts

I purchased a Skutt 1027 (Kiln Sitter)from someone who owned if for 2 yrs but it was new. It's never been fired. It was a 3 phase, my husband converted it to a single phase. (He does electrical/talked w/Skutt beforehand)  Kiln is hardwired into electrical box. 
He drilled the holes in top and bottom as instructed, mounted a blower (190 cfm)on the wall behind kiln. Overhead he mounted a strong exhaust fan (it's a kitchen fan that was over a 6 burner gas stove previously) it is vented out the back of our home to outside. ..  We did the match test over the holes on top of the kiln and it pulled air well.  
My questions are- he drilled a 1 1/2" hole in tubing going to blower to make sure it got enough fresh air. (Do not want to burn up the blower fan) .. should he add another hole higher on the tubing? (Note phote marked w/blue circle) 
Also,  the power cord for the blower is hanging behind the kiln. He said he could hardwire the fan and give me a switch to flip instead.  Seems this power cord could easily be damaged hanging down?  

This is my first studio and kiln, we want it to be right. Suggestions, thoughts? 

holes for blower to breathe.jpg

Our set up.jpg

Front view w exhaust.jpg

Blower plug behind kiln.jpg

Link to comment
Share on other sites

Looking closer he has one exhaust discharging and hopefully being picked up by the range hood. This won’t work so well especially for very light volatile particles as they will be ejected into the room before being completely removed.

The fan for the kiln is axial and will need a bunch more room air to keep itself cool. The range hood on the other hand is great for heat and fumes and will cool itself with room air.

Here is something to watch (old) that may give a better sense of the quantities we are talking about.

https://youtu.be/etpa2Pc9Hug

I would almost prefer just the range hood at this point. I can’t think of a good way to combine both of these really other than to pipe the kiln fan into the discharge of the range fan and install back draft dampers on both which will leak when one or the other is idle.  And still the axial kiln fan will need a bunch of room air to keep it cool and not overdraw the kiln.

Just my initial thoughts ………

 

 

Edited by Bill Kielb
Link to comment
Share on other sites

A downdraft vent is good because it will increase element life and decrease corrosion of the kiln's metal parts. However, like Bill said, having it blow out into the hood is probably not very effective at removing the fumes from the room. With big powerful hoods it'll work pretty well, but not so much with a cooking hood. The hood is not going to catch everything. I would run the downdraft duct all the way to the outside. As for whether or not it needs more fresh air holes, you'll need to measure the temperature of the air in the duct. It should be under 140F. It's a balance between pulling enough air from the kiln to remove the fumes, but not so much that you're bringing too much cold air into the kiln and making it work harder. Ideally, the fresh air hole in the duct should be right at the kiln. Otherwise you're pulling really hot air through that flexible duct, which isn't safe and will degrade the duct very quickly. You're trying to keep the ductwork cool as well as the vent motor.

Link to comment
Share on other sites

My understanding of the physics (fluid dynamics) behind the downdraft vent is that the box under the kiln (L&L calls it the bypass collection box, Skutt calls it the plenum cup) has an opening on the opposite side from the hose connection so that the fan at the output on the far end of the system can pull a significant volume of room air through the box and thus create a venturi effect to draw the kiln fumes down through the holes in the base of the kiln. The L&L collection box has an adjustable "sliding valve" to regulate the amount of room air drawn through the box (thus adjusting the venturi suction across the holes in the kiln base) while the Skutt plenum cup just has a hole. This flow of room air also serves to cool whatever fumes are being drawn out of the kiln and up through the fan. The system does not apply direct suction to the holes in the kiln.

Because air flows seek the path of least resistance, the hole in the pipe of your vent will both increase total air flow at the fan and reduce suction at the base of the kiln when everything is in good condition. However, it introduces the necessary cooler room air at some distance after the fumes leave the kiln. Also, your design with the fan in the middle of the duct run provides the appropriate negative pressure from the kiln to the fan, but applies positive pressure after the fan, blowing the exhaust into the stove hood in hopes that it will be picked up. As Bill notes, this may not work, but also as the duct work corrodes over time (it will, count on it), the positive pressure will blow the stinkies back into the room long before they come out by the stove hood. The design of the Skutt and L&L systems places the fan right on the outside wall of the room so that the whole system remains under negative pressure until being exhausted to the outside. Then, any minor leakage in the duct work will draw air in, not push the fumes out.

Link to comment
Share on other sites

4 hours ago, Dick White said:

The design of the Skutt and L&L systems places the fan right on the outside wall of the room so that the whole system remains under negative pressure until being exhausted to the outside.

Ideally, yes. In reality, not very often. Mounting the fan directly to the wall makes it a lot more difficult to deal with when the motor needs replacing, and makes it more difficult to critter proof. The simplest and best looking installation for a home setup is to install a standard dryer vent  duct with the flap and critter cage on the outside, mount the vent fan to the wall inside near it, and connect them with an elbow or short flexible duct. For venting through the roof, like some homeowners and 95% of schools do, the fan motor is mounted near the kiln, and many feet of duct exist between the fan and the exterior. The specs for the vents are that they can handle up to 60 feet of duct and 3 elbows. Ideally you want the fan as near to the exterior as possible, but with a 6 foot power cord that's not going to happen in most situations. The good news is that the ductwork between the fan and the exterior is almost always hard duct, which if installed properly with sealed seams, is very unlikely to leak. The majority of duct corrosion happens between the kiln and vent motor, and galvanized rigid duct will last a pretty long time.

Link to comment
Share on other sites

2 hours ago, Honeyhas6 said:

I just found out the overhead (kitchen) exhausted outside is 120 cfm on low, 190 on medium and 550 cfm on high or (boost, it's called) .. 
 

As much as I like down drafts, for your situation I still don’t have a good idea to make use of both fans. The range exhaust at 500-600 cfm on max is typical design for these things which is a great option to have to remove heat. For all practical purposes All pressure ductwork will leak a little, all of it, always, all the time. Do your best to seal it nicely, maybe foil tape all vertical seams, and joints including elbow joints to minimize to well below 1%. If this duct extends above the garage into an unheated attic space, you may need to insulate it to prevent winter condensation from forming and rusting out the ductwork. Looking at your southeast location, it may not be an issue.

Save the downdraft for another day and improved design using a proper mixing manifold mounted on the kiln and next time enough dilution air to keep it running cool with that particular axial fan which uses its own exhaust to keep the motor windings cool.. If he watches the video above, that fan easily can serve two kilns and a full exhaust grill to ensure enough air is present for cooling the motor and ductwork. If that fan only draws air through a couple small holes it will be starved for cooling.

The simplest application I have seen for this type of (axial) fan is a full open tee below the fan with the duct running down to the kiln. Even with such a large hole in the duct it will still draw several tenths of an inch suction at the kiln mixing plenum.  You only need a tenth of an inch (-0.1” wc (suction)) at that point to perform like the store bought.

Edited by Bill Kielb
Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.