Can I use an adapter from nema 14-50 to 6-50 for my kiln?


Recommended Posts

That would qualify as an extension cord, which is not recommended for kilns. Just change the outlet. Make sure the wiring and breaker are the correct size for the new kiln. The old outlet is a 4 wire system, probably 2 hots, 1 neutral, 1 ground, unless it was a 3 phase system which would be 3 hots and a ground. Either way, with the new plug you'll need two hots and a ground, no neutral. You can either remove the extra wire or just leave it there but tape it off at both ends.

Link to comment
Share on other sites

Archived

This topic is now archived and is closed to further replies.

×
×