32 minutes ago, emmauswalker2 said:

Just changed the elements and relays on TNF82 series kiln and doing a test fire.  The error code HTde came up, but is steadily going up in temp.  What should I do?

As I recall it is the high temperature deviation  and comes factory set at 100 degrees. I believe it is the amount that the kiln can exceed the setpoint until an alarm is generated. Setting is something between 18 degrees and 200 degrees  from memory. Check your sentry manual and it will detail. Since your kiln is operating I would just check what alarm setting sensitivity  is currently entered in  for htde.  18 would be your most sensitive amount and 200 degrees the least sensitive.